Is this fire wall properly built? Specifically the drywall isn’t continuous behind the ceiling track. Multi story concrete structure that was turned into condominiums. Unit I’m in had 2 layers 5/8” uninterrupted, fire caulked top and bottom. Located in MA.

2 Upvotes

13 comments sorted by

9

u/This_dumpsterfire Building Official 5d ago

Fire wall, fire partition, fire barrier. This is not a fire wall. We wouldn't know for sure without the listed assembly.

2

u/Nine-Fingers1996 Residential Contractor 4d ago

I should’ve used a better description. 1 hour fire rated wall assembly is the proper description.

2

u/sfall consultant 4d ago

you need to see how the floor/ceiling assembly is rated. if the rating does not include the ceiling drywall it is built wrong for a fire barrier or fire partition

1

u/IHerebyDemandtoPost 4d ago

The building code has three types of fire-rated walls: fire partitions, fire barriers, and fire walls.

Those are listed in order of lowest to greatest level of fire separation.

When you speak to code officials, don’t say fire wall unless you mean the third, most restrictive, category.

2

u/MVieno 5d ago

To expand on this a little bit.

You mentioned condo. That implies that this is in a building that has more than 2 residential units in it, which kicks it from residential building code to commercial building code. This is important because “fire wall” has different meanings based on the code you are using.

An IRC “fire wall” is more or less equivalent to an IBC “fire barrier.”

What we can see in your photo is not, and will never be, an IBC fire wall. It can be a fire barrier or a fire partition, though.

Typically residential units in multi family housing have a mix of both fire barriers and fire partitions, but only rarely have actual fire walls.

To throw a wrench in, there is ALSO fire-rated construction, which has different requirements from the other types of walls/partitions mentioned.

As someone else said, we’d all need to see the actual building code sheets to see what is required in your photo.

3

u/IHerebyDemandtoPost 5d ago

Specifically the drywall isn’t continuous behind the ceiling track.

Then no.

Firewalls must be continuous from foundation to roof.

There is only one exception for podium buildings.

2

u/picklesuitpauly 5d ago

Find the listing they used, bet it has to be continuous. Also we don't allow romex in steel studs even with bushings.

1

u/Novus20 5d ago

Why would they not run the wall right up to the underside of the concrete floor…….JFC

1

u/RuskiGrunt 4d ago

No I doubt it. Look at the plans the assembly is more likely to be called out as a fire barrier or fire partition instead of a fire wall for walls separating units. Fire Walls in multifamily construction are more serious and they divide buildings as a whole to reset travel distances on bigger buildings. That drywall doesn't even look like its 5/8". Obviously the wall is not completed. The outlet box does not have puddy pads on it. I am also not sure what the insulation is there for, just for soundproofing? Is that mineral wool or fiberglass?

0

u/GenConfusion 5d ago

why would you need a firewall in a concrete structure to begin with unless it's separating it from a wood structure?

1

u/Mental_Ad3737 4d ago

To separate dwelling units

1

u/GenConfusion 4d ago

That's not a firewall though.

1

u/Mental_Ad3737 4d ago

Its a fire rated vertical assembly and fire rated horizontal assembly